    Rewinding 165va to 127

    Is there any issues with winding a 165va transformer down to 127? it's an off the shelf hammond?

  2. #2
    Join Date
    Dec 2003
    Posts
    24220
    Do you mean 165VA or 165VAC?
    If VAC, Not usually, you can either try and determine the turns/volt ratio ahead, by winding on 5~10 turns of enameled wire, gauge does not matter,
    And measure the resultant AC.
    Or take a guess and figure 2t/v and give it a try, trouble is it is a pain if you take off too much.
    Al.
    CNC, Mechatronics Integration and Custom Machine Design

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.

  3. #3
    Join Date
    Jan 2005
    Posts
    183
    12v 20 amp to 9v 15 amp

  4. #4
    Join Date
    Dec 2003
    Posts
    24220
    the VA rating will remain the same, whatever you do to the winding, the problem comes when you want to decrease the voltage and increase the current for a given VA, in that case the winding may not be rated for that current, but if you are dropping the voltage and running at a lower current, or increase the voltage and decrease the current, then you are still within the VA rating of the transformer. (9x15 is less than 12x20).