587,380 active members*
4,174 visitors online*
Results 1 to 9 of 9
    Sep 2004
    6
    photoelectric switch circuit
    I want to be able to activate the coil of a relay with a photoelectric switch.
    The switch is 24VDC, 100ma load. The relay is also 24VDC, 1.5VA (1W) consumption.
    Am I correct in calculating that the relay has a draw of .04 amps and that the sensor will be able to drive this relay? Anything else I should be aware of?
    Dec 2003
    24223
    DC power is IxV, VA is usually used to indicate AC power rating due to inductive effects.
    If the P.E. switch is 100ma max, then the coil on 24vdc requires a resistance of 240ohms or less, most manufacturers state coil resistance in the specs.
    Al.
    Albert E.
    Sep 2004
    6
    I don't see a ohm rating in the specs.
    Input circuit
    Supply voltage:
    24V DC terminals A1(+)-A2
    voltage selector engaged
    24V AC terminals A1-A2
    110 to 240V AC terminals A1-A2
    voltage selector not engaged
    Tolerance:
    24V DC ±10%
    24V AC -15% to +10%
    110 to 240V AC -15% to +10%
    Rated frequency: 48 to 63Hz
    Rated consumption:
    24V AC/DC 1.5VA (1W)
    110V AC 2VA (1W)
    230V AC 8VA (1.3W)
    Duration of operation: 100%
    Reset time: 100ms
    Residual ripple for DC: 10%
    Drop-out voltage: >30% of the supply voltage
    http://www.maxicont.hu/doc/termekek/...TA/en_d6dq.pdf
    Thanks for your help.
    Dec 2003
    24223
    It would appear that the rated power consumption on DC is 1 watt so on 24vdc the current would ~42ma.
    Al.
    Albert E.
    Sep 2004
    6
    Thanks for the help!
    Jan 2006
    738
    Put a heafty diode across the coil (A1 A2) in reverse polarity or you may quickly kill the output of the photoswitch. The inductive kickback from the coil can be a very high voltage spike of opposite polariity to the supplied voltage. This is common practice.
    http://www.allaboutcircuits.com/vol_3/chpt_3/9.html
    Hope you read this in time.
    Steve
    Dec 2003
    24223
    I would suspect that you may only need the back EMF diode if fitting an external relay as in the dotted line. As I imagine that if using the internal relay that would be taken care of?
    Al.
    Albert E.
    Sep 2004
    6
    Quote Originally Posted by vger View Post
    Steve
    So would a IN4001A diode do the job?
    Al.
    I'm not sure what dotted line you're referring to.
    Dec 2003
    24223
    The diagram appears to show the internal relay and contacts, there is a dotted line with S switch and a external relay to the R.H. side.
    Presumably to switch a heavier duty relay? (1VA A2-B1)
    If you use the external type a IN4001 should be OK.
    Al.
    Albert E.
  1. Is it possible to use the home switch as the limit switch as well?
    By Darc in forum Mach Software (ArtSoft software)
    Last Post: 11-02-2012, 06:25 PM
  2. limit switch- home switch
    By normd in forum CamSoft Products
    Last Post: 05-17-2008, 12:56 AM
  3. limit switch and home switch setup
    By Runner4404spd in forum CNC Machine Related Electronics
    Last Post: 12-15-2005, 02:58 PM
  4. Limit Switch / Home Switch in Software
    By Sanghera in forum CNC Machine Related Electronics
    Last Post: 11-02-2004, 12:58 AM