    Unhappy Fanuc I/O Problem?

    I've been struggling :boxing: with a Bridgeport VMC machine with a Fanuc 11M controller for a long time.
    the motherboard was changed because apparently it had a problem (not booting at all),
    after the change the machine boots but shows an alarm as if all limit switches were tripped.
    my guess was that the IO module had a fail, then replaced it but no change.
    finally I read that i have to check the optic fibers and if there are the IR signals.
    i test that using an infrared camera and could see a solid IR lights coming out from motherboard and IO module. Now I don't know what else to check.

    Jorge B.
    Jorge B.
    jorbercnc.com

  2. #2
    Join Date
    Apr 2009
    Posts
    1379
    when posting, give complete information, please.
    What are the alarm #s? Did you look in the diagnostics to see the input signal states? Is there a ladder? Does it show the signals (ot) active?

  3. #3
    Join Date
    Dec 2003
    Posts
    24220
    Is there a 24v supply dead? is 24v present on the I/O board the O.T. switches are input to?
    Make sure the fuse on the I/O board is OK.
    See similar post http://www.cnczone.com/forums/fanuc/...uit_limit.html
    Al.
    CNC, Mechatronics Integration and Custom Machine Design

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.

  4. #4
    Join Date
    Apr 2004
    Posts
    61
    Quote Originally Posted by memoryman View Post
    when posting, give complete information, please.
    What are the alarm #s? Did you look in the diagnostics to see the input signal states? Is there a ladder? Does it show the signals (ot) active?
    There is voltage even in the module i can see the leds change when any of the limits is pressed. The alarms are only for the limits OT +X - X +Y - Y +Z - Z.
    What is happening is that these signals are not getting in the motherboard
    have to look for the fuses I think I already did but going to double check
    Jorge B.
    jorbercnc.com

  5. #5
    Join Date
    Apr 2009
    Posts
    1379
    It is possible that the machine is wired with all ot switches in series (very rare); check the machine wiring diagrams.
    You should be able to see inputs in the diagnostics. Do you see a response when an ot is activated?

  6. #6
    Join Date
    Apr 2004
    Posts
    61

    still looking

    Quote Originally Posted by memoryman View Post
    It is possible that the machine is wired with all ot switches in series (very rare); check the machine wiring diagrams.
    You should be able to see inputs in the diagnostics. Do you see a response when an ot is activated?
    I was checking what you Al and Memoryman told me to check, What I found is that the 24 V are present on the I/O module, i tested the fuses and all are ok, in the diagnostics and in the ladder when I press any button on the operators panel I can see that is been activated(cycle start, dry run, etc), different happens when I press any of the limis switches, I only can see on the module leds but neither in the diagnostics nor in the ladder, they are seen as if were not pressed. I am still thinking that is a problem of comminication between the I/O and the Master PCB.
    Attached Thumbnails Attached Thumbnails IMG_20121016_112224.jpg   IMG_20121016_114059.jpg   IMG_20121016_114310.jpg   IMG_20121016_112202.jpg  

    Jorge B.
    jorbercnc.com

  7. #7
    Join Date
    Apr 2009
    Posts
    1379
    It looks that the communication is done through an optical cable; it is very unlikely that there is a problem with that.
    Do you have a ladder diagram? Machine electrical? There is probably a common wire/signal to the limit switches. Look there.

  8. #8
    Join Date
    Dec 2003
    Posts
    24220
    Try hold opening the contact on one of the switches (N.C.?), measure the voltage between the contacts, normally the inputs are sourced and sunk to ground through the switch, either way, you should see 24v present at one point and go to zero when you close the contact.
    Al.
    CNC, Mechatronics Integration and Custom Machine Design

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.

  9. #9
    Join Date
    Apr 2004
    Posts
    61

    24V ok

    Quote Originally Posted by Al_The_Man View Post
    Try hold opening the contact on one of the switches (N.C.?), measure the voltage between the contacts, normally the inputs are sourced and sunk to ground through the switch, either way, you should see 24v present at one point and go to zero when you close the contact.
    Al.
    I did that on the module and is exactly as you describe, see picture
    Attached Thumbnails Attached Thumbnails testmodule.jpg  
    Jorge B.
    jorbercnc.com

  10. #10
    Join Date
    Dec 2003
    Posts
    24220
    I had thought you had a remote I/O board, but I see you have a remote PLC rack.
    Usually with these systems even though the LED lights, which shows the input is toggling, it is just a local indication, it does not guarantee that the signal is getting any further.
    Does it only apply to inputs on that one card? and do the other cards register and show I/O in the diagnostics? If so, it means the PLC is communicating.
    Al.
    CNC, Mechatronics Integration and Custom Machine Design

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.

  11. #11
    I assume this all worked before the motherboard was replaced (Before the non boot issue) That being said looks like you have a bad motherboard. It fixed the booting issue and gave you an I/O issue. Might want to replace the motherboard again.

  12. #12
    Join Date
    Apr 2004
    Posts
    61
    thanks drdos, that's what I suspect is happening. I am trying to enclose the problem to make sure what would be the solution


    Quote Originally Posted by drdos View Post
    I assume this all worked before the motherboard was replaced (Before the non boot issue) That being said looks like you have a bad motherboard. It fixed the booting issue and gave you an I/O issue. Might want to replace the motherboard again.
    Jorge B.
    jorbercnc.com

Similar Threads

  1. Fanuc 15T IPL problem
    By lshingleton in forum Fanuc
    Replies: 4
    Last Post: 08-30-2012, 04:23 PM
  2. Fanuc Oi-TA LCD problem
    By rai in forum Fanuc
    Replies: 6
    Last Post: 01-31-2012, 01:00 PM
  3. LSK problem with my fanuc
    By samiahmed in forum Fanuc
    Replies: 9
    Last Post: 03-08-2010, 09:40 AM
  4. fanuc 10M problem
    By mohammad reza in forum Fanuc
    Replies: 12
    Last Post: 09-02-2009, 02:06 PM
  5. Fanuc 21i-T DNC Problem
    By Stebedeff in forum Fanuc
    Replies: 4
    Last Post: 07-16-2007, 09:00 PM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •