HI,
I would like to know if you ever got it going?
I also am several $$$$$$ from 3 phase bliss.
I spent $3600.00 on a 45hp rotophase and $2400.00 on a multitap transformer.
As I get at times 257 ac v.(perfectly normal they say at Hydro Quebec).
It all has to work like this.In comes 220 v more like 257v, thru rotopase out comes 3 phase then into 220v to 600v custom multitap copper x0 transformer.
Custom because no one has multi super duper multi tap transformers for perfectly normal hydro power....
This power then runs my colchester storm total hp rating25hp.Which has a 600v step down to 220v transformer?
I tried going 220v direct but the fanuc control would crash when I turned on the comet mill which is rated at 25hp also.
After fiddling with the taps I finally got it all stable.
I can run both the lathe and mill and a 5hp angle roll at the same time without crashing anything.
But last week the spindle drive in the lathe malfuntioned(Quit).....
I hope its not from the roto setup I have.
The power going into the power pack 229,230,235v should be correct.
I suspect hydro ,as not long before the malfuntion the lights in the shop dimmed a little!?
Can power surge protection be fond in this power range?
So many questions so little time.
Thanks
Claude