586,634 active members*
3,004 visitors online*
Register for free
Login
Results 1 to 8 of 8
  1. #1
    Join Date
    Feb 2016
    Posts
    10

    What to do with wire shielding???

    I am using shielded wire between the drivers and the steppers as well as the VFD and the spindle. My question is what do I do with the shielding in the cable? Do I ground it on the sending end, receiving end, both ends or neither end?

    Thanks!

    Matt

  2. #2
    Join Date
    Feb 2009
    Posts
    2143

    Re: What to do with wire shielding???

    Ground on 1 end
    CAD, CAM, Scanning, Modelling, Machining and more. http://www.mcpii.com/3dservices.html

  3. #3
    Join Date
    Dec 2003
    Posts
    24223

    Re: What to do with wire shielding???

    If equi-potential bonding is done on the machine to the star point ground, then both ends can be connected to ground.
    Al.
    CNC, Mechatronics Integration and Custom Machine Design

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.

  4. #4
    Join Date
    May 2015
    Posts
    1422

    Re: What to do with wire shielding???

    ^^ it often won't be though, especially on cheaper machines.

    I'd pin all your earths back to one star point. Earth from incoming mains cable goes there, as do any earth points from power supplies, VFD, stepper drivers, logic boards and all the shields. This avoids ground loops and the potential differences they cause.

    oops - missed a bit. The far end of the shields? Leave them disconnected.

  5. #5
    Join Date
    Dec 2010
    Posts
    70

    Re: What to do with wire shielding???

    ^ right!

    mobile...
    HTM.Ro - Hobby Tools Manufacturing

  6. #6
    Join Date
    Feb 2016
    Posts
    10

    Re: What to do with wire shielding???

    This is interesting. I was told previously to keep D/C grounds separate from A/C grounds and in fact to keep D/C grounds from different power sources also separated (e.g., PC USB 5v ground separate from toroidial 5v ground). Do you guys feel this previous advice is wrong?

    - Matt

    Quote Originally Posted by dharmic View Post
    ^^ it often won't be though, especially on cheaper machines.

    I'd pin all your earths back to one star point. Earth from incoming mains cable goes there, as do any earth points from power supplies, VFD, stepper drivers, logic boards and all the shields. This avoids ground loops and the potential differences they cause.

  7. #7
    Join Date
    May 2015
    Posts
    1422

    Re: What to do with wire shielding???

    Matt, I guess the answer is "it depends". Not sure it's so much AC/DC separation as much as partitioning high power and small signal areas. But consider: they must be grounded in common at some point. If it's not in the machine, it's in the powerstrip feeding the computer and power supplies on a small machine, or in the switchboard on a larger machine. Somewhere, they all hook up. I'm a fan of keeping the runs (and therefore impedances, and therefore the voltage differentials for given current draws) to a minimum from that one point where everybody agrees what 'zero' is.

    But, sure, if you have a massive but crappy VFD shoving a tonne of noise back down into the earth, attempting to isolate that isn't a bad idea. Just be careful when you do, though: the motor windings will inductively couple to the casing and induce currents (and therefore voltages) there which, if not pinned to a common ground, can cause serious mischief.

    Exactly what was happening on my router. Motor etc were 'isolated' as was all the logic board but charge built up enough over several hours of running that I got a significant belt when I touched the case trying to work out why the computer would lose the BOB whenever I turned the spindle down. Sorted out the earthing with a big ol' fat spark as I connected the earth strap and since then it's not missed a beat.

  8. #8
    Join Date
    Dec 2003
    Posts
    24223

    Re: What to do with wire shielding???

    There are several papers out there published by the likes of Siemens, the PDF used to be on their web site, unfortunately since they revamped their web site it does not show up, but also details the now preferred method of grounding both ends..
    It covers grounding and equi-potential bonding, of which the aim is to prevent ground loops and most industrial CNC systems do this, this allows the preferred choice of grounding both ends of shielded cables.
    Equi-potential bonding also avoids problems caused by spurious noise.
    http://www.cnczone.com/forums/phase-...se-issues.html
    Al.
    CNC, Mechatronics Integration and Custom Machine Design

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.

Similar Threads

  1. connecting shielding
    By Beargesen in forum Gecko Drives
    Replies: 13
    Last Post: 01-21-2024, 09:34 AM
  2. DB9 shielding wiring
    By TheBulk in forum DIY CNC Router Table Machines
    Replies: 2
    Last Post: 03-11-2011, 03:42 AM
  3. wire shielding / screening
    By mtompson in forum CNC Machine Related Electronics
    Replies: 0
    Last Post: 03-20-2008, 09:29 AM
  4. EMI shielding
    By bigalow in forum CNC Machine Related Electronics
    Replies: 2
    Last Post: 02-29-2008, 03:18 PM
  5. Connection of shielding
    By cncuser1 in forum CNC Machine Related Electronics
    Replies: 2
    Last Post: 06-18-2006, 01:57 AM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •