    need help on milltronics cent 1 install index rotary table

    hi we have a milltronic cent 1 old control, need help
    how to hook up the hass index, anyone own a milltronic
    with indexer

  2. #2
    Join Date
    Dec 2005
    Posts
    61
    See attached docs.
    Attached Files Attached Files

  3. #3
    Join Date
    Nov 2004
    Posts
    70
    ok i hook up exactly like in the blueprint
    red wire go to misc 11pin
    blue ground
    black to the relay tb1 spare relay common
    white to relay tb3 spare relay no contact
    and i hook up another wire wire fr tb7(is 24volt) to mics 13 pin
    wrote program 9025
    M65
    G4P.5
    M75
    M32
    PROGRAM 9027
    (DO NOT REMOVE)
    SET X7
    CLR X7
    change in the parameter m code
    9025 to 71
    9027 to 65
    all done
    in the haas index
    pp1 to #1 relay pulsed for 1/4 second at the end
    pp2 #1 normally close.

    wrote short program
    M71
    G1 X3
    test it not woking.
    in the screen x input wait channel 0 for open
    when press cycle start M71 await channel change to 1 flashing 1 and 0
    M FUCTION still on 0
    however the index not rotate.

    can you explain how is the mics pin 11 talk to the index and how
    mics pin 13 work when hook up with the tb7(24 volt)
    thanx you

  4. #4
    Join Date
    Dec 2005
    Posts
    61
    Misc 13 turns on the relay to activate the cycle start on the indexer.
    Misc 11 is the signal for the wait channel as long as it is grounded it will the cnc will wait.
    The indexer may need more time to start you can put a dwell between the set x7 and clr x7 make it
    SET X7
    G4P1
    CLR X7
    this will make it wait 1 second.
    The indexer must have the parameter set so the indexer done signal is normaly closed

  5. #5
    Join Date
    Nov 2004
    Posts
    70
    when i test M71 MISC pin 13 still on 0 didn't turn to 1
    to turn on the relay.
    and mis pin11 keep flashing 1 and 0 constantly.
    in haas pp2 i set it to normally close.

    program 9025 and 9027
    M code custom m71 m65

    which program control for the wait channel msc 11
    and mics 13 is there a way to test if the signal coming out those
    pin

  6. #6
    Join Date
    Dec 2005
    Posts
    61
    Misc 11 is the wait channel. this needs to have a ground while it should be waiting. When it is grounded under the diag X in 7 should go to a 1.
    Then make a program that is M32 then some sort of axis move.
    The machine sould just sit until you remove the ground from misc. 11

  7. #7
    Join Date
    Jan 2007
    Posts
    333
    I can't find what M32 is/does.
    Anybody know?
    Thanks in advance.

  8. #8
    Join Date
    Dec 2005
    Posts
    61
    M32 tells the control to wait for the wait channel

  9. #9
    Join Date
    Jan 2007
    Posts
    333
    Thanks mholden,
    A guy was using this on his Cent 5:
    _
    N1 PULSE1Y12 (OUTPUT WIRE FROM PLUG Y-OUT TO FIRE INDEXER)
    N2 G4 X.5
    N3 IF PIN[1006]=0 GOTO 2
    -
    This would work most of the time but he experienced intermittent lockups. His PULSEx parameter was set for 500 milliseconds.
    I'll tell him about M32.