Originally Posted by
SCzEngrgGroup
A 4-wire connection to a 220V machine has no benefit. In the US, houses are wired with 220V "split phase", which is two 110V "legs" that are 180 degrees out of phase. Any 220V appliance will use the two "hot legs" and a ground. The neutral wire is needed ONLY if that appliance ALSO uses 110V. As an example, some kitchen appliances, particularly stoves and ovens, will use a 4-wire connection so they have 220V for the heating elements, and 110V for the lights and perhaps electronics. In much of the rest of the world, houses are provided with 220V single-phase, so the three connections are "hot", neutral, and ground, and there is NO 110V usage.
If, as I would assume, the Tormach is provided wired for a 3-wire cord, those three wires will be a ground, and the two "hot" legs in the US, or the one "hot" leg and a neutral in most of the rest of the world, and there is absolutely nothing to be gained by adding a 4th wire - there will be nothing to (correctly) connect that neutral wire to, and tying it to the system ground actually creates a safety hazard.
Regards,
Ray L.