    220v Outlet Questions

    Okay, I've got my outlet wired up. I am using a 30 amp breaker. A black wire leads from one pole, a white from the other and of course the ground goes to ground. I am using a heavy duty 2 pole air conditioning outlet. I run the black to one pole on the outlet, the white to the other pole, and the ground obviously to ground. Or should I combine black and white to one pole and run another wire to Neutral (I don't think this is the correct way, but want to be sure)? Does any of this sound incorrect?

    Now here is the real questions. I am using this outlet to run a fenner contrex m-drive to run my spindle's motor. The drive states that it can use 110-220 as input. So for my wiring, I want to run one pole of the outlet to L1, the other pole goes to Neutral/L2, and ground to ground. Does this sound correct?

  2. #2
    Join Date
    Dec 2003
    Posts
    24220
    If you are wiring the spindle drive from a 220v outlet, then you use the L1 L2 to 220v the neutral does not enter the picture, not in N. America, anyway.
    Do not connect any neutral to ground anywhere but at the panel.
    If you are connecting this up to 220vac outlet then you have 2 'hot' conductors and a ground.
    Al.
    CNC, Mechatronics Integration and Custom Machine Design

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.

  3. #3
    Join Date
    Mar 2007
    Posts
    137
    Al,
    The motorhome bays around Grand Rapids Michigan, now all have 230 volt single phase plugs with ground and neutral. I dont know if thats new code or maybe just if your over a certain amperage or what. 230 single phase don't enter into my world very often.
    Buck

  4. #4
    Join Date
    Dec 2003
    Posts
    24220
    Quote Originally Posted by springlakecnc View Post
    Al,
    The motorhome bays around Grand Rapids Michigan, now all have 230 volt single phase plugs with ground and neutral. I dont know if thats new code or maybe just if your over a certain amperage or what. 230 single phase don't enter into my world very often.
    Buck
    Yes, that is probably to support both 240v and 120v & neutral circuits, but it would appear in this case the neutral is not needed.
    Or that is the way I interpreted it.
    In other words, if you are not using, or don't need the neutral, don't run it.
    Al.
    CNC, Mechatronics Integration and Custom Machine Design

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.

  5. #5
    Join Date
    Jan 2006
    Posts
    461
    Got it Al. Thank you.

Similar Threads

  1. which 220v mig to get?
    By keebler303 in forum Welding Brazing Soldering Sealing
    Replies: 5
    Last Post: 12-14-2006, 04:06 PM
  2. bp heidenhain 440v to 220v
    By CASTLEVILLE in forum Bridgeport / Hardinge Mills
    Replies: 6
    Last Post: 12-06-2006, 11:40 PM
  3. 220v acceptable range from power co.?
    By jderou in forum CNC Machine Related Electronics
    Replies: 1
    Last Post: 11-06-2006, 04:58 PM
  4. Yet another 120v to 220v
    By Konstantin in forum CNC Machine Related Electronics
    Replies: 4
    Last Post: 02-24-2006, 08:57 PM
  5. Gecko Factory outlet...and more
    By Bloy2004 in forum Gecko Drives
    Replies: 27
    Last Post: 12-30-2004, 11:25 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •