    PMC bit toggling?

    Hi, does anyone know why I would not be able to go into force mode and toggle bits in the pmc on a Fanuc 180i-TB but can on the 30i? There must be some parameter that is set to enable this that the machine builders turn off. I am using Ladder III software for programming ladder logic.

  2. #2
    Join Date
    May 2009
    Posts
    181
    is programmer write enable on?

  3. #3
    I know on the oi's you have to enable the force on off button in the <oprt> soft key to the right of the force menu softkey
    ************************************************** *********
    *~~Darwinian Man, though well-behaved, At best is only a monkey shaved!~~*
    ************************************************** *********
    *__________If you feel inclined to pay for the support you receive__________*
    *_______Please give to charity https://www.oxfam.org.au/get-involved/_______*
    ************************************************** *********

  4. #4
    Join Date
    Mar 2007
    Posts
    25

    Got it!

    Actually figured it out. Parameter 900 (keep relays), bit 4 needs to be a 1 in order to go online and toggle bits and bit 1 needs to be a one in order to do online edits!!!! :banana: