  1. #121
    Join Date
    Nov 2010
    Posts
    59
    correction, the first transformer is fed from two phases @ 240v = 415V each into 0v and 415V giving me no where to go to reduce the voltage on the taps, pretty strange getting a potential of 240v from the 0v tab to earth ! At least I have learnt something today, just because the transformer has a 0v tab, dont mean its connected to 0v

    I guess I am going to have to take turns off the transformer, is there a post and or pictures of the proceedure ?

  2. #122
    Join Date
    Dec 2003
    Posts
    24223
    You mention this transformer is fed across two phases, this represents a 415 single phase transformer, the star or neutral is not used.
    If you want to reduce the secondary, it is usually wound on last, if so you are in luck as you take turns off as needed, and you can calculate as a minimum that there will be around 1.5 to 2 turns/volt.
    With a square lamination type it is a bit uglier than doing it on a toroid, but it is possible with care.
    Al.
    CNC, Mechatronics Integration and Custom Machine Design

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.

Page 7 of 7 567

Similar Threads

  1. Retrofit advice on Hurco km3P
    By Jackal66 in forum HURCO
    Replies: 7
    Last Post: 10-27-2010, 02:58 AM
  2. Hurco KM3P won't zero home in x axis
    By Jackal66 in forum HURCO
    Replies: 6
    Last Post: 05-29-2010, 03:09 PM
  3. Hurco KM3P
    By ivanfed in forum HURCO
    Replies: 0
    Last Post: 04-20-2009, 10:48 AM
  4. Hurco KM3P HELP
    By winds1sj in forum HURCO
    Replies: 7
    Last Post: 12-20-2008, 08:44 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •