Re: Toroidal PS and E-stop contactor circuit and EdingCNC
Originally Posted by
catahoula
Yeah that seems reasonable to me. The PrintNC diagrams as well as the Centroid Acorn manual both recommend the contactor circuit, and I understand the idea that the E-stop is not a normal use function but a last resort so having redundancy built in may be appropriate. But the VFD is already going to be controlled by a relay/contactor so it does seem a bit overkill.
Hi,
I would suggest that you follow the lead of the CNC manufacturers and have your Estop remove AC power from the drives and spindle. Leave the motion controller powered off Its 24vdc or other dc power.
Removing AC power from the drives and VFD is safe and easy to do. There really isn’t a reason not to do it.
As to your relay controlling the VFD, many breakout boards/ controllers use FETs to turn the relay On/Off. when a FET fails, the majority of time it fails in the on state, meaning that the VFD will not turn off if you press a software Estop.
This issue is also the failure mode for solid state relays. It’s why mechanical relays are used in contactors.
If you’re CNC system can’t harm anyone then maybe you don’t even need an Estop, but once you VFDs and spindles then it should be controlled by a proper EStop circuit.
Cheers
Peter
Sent from my iPhone using Tapatalk Pro
-------------------------------------------------
Homann Designs - http://www.homanndesigns.com/store