Originally Posted by
chiefcnc
PE ( this is earth ????)
Also on VFD & Not sure which ones go from VFD to Spindle
U/t1 ????
V/t2 ????
W/t3 ????
I have also noticed a separate earth input below the main PE input on VFD. Is this for earthing the VFD to example metal cabinet?
Besides the earth there is a J1 (not sure what this is?
You don't have the manual for this? They are all on line.
The PE is for the Earth ground conductor and should receive the service ground conductor ran with the L1/L2/L3, the ground conductor to the motor frame should also be connected to this terminal.
The U,V,W are the three phases to the motor.
Al.