Azam, you have quite a few programming errors now.... if you call factory for help they will tell you to go back to default settings and start over.... here are a few of the problems you have introduced and need to fix. I will go thru past posts:
A003 = 60 not 300 - YOU were correct. it is the base freq of your motor. ur 300 will starve ur motor so bad it probably will give - ready? E05 overload error.
A013 =10% is not good for mach3 control; put it back to 0% so mach 3 can control it right.
A2xx parameters ARE for second motor spec set. since u r not using a second motor parameter set, these have NO meaning to u or ur drive. change if u want practice changing parameters, but that will do nothing good or bad.
A004 IS the max freq (speed) u want ur motor to go. so if u want, set it to 300: 300/60= 5x base speed. BTW, this is EXTREMELY HIGH. If u know ur mechanics and ur motor can handle this (1800*5= 9000rpm!!) go for it, but I would bet a full case of GOOD beer ur motor and machine cannot handle it. If u do run it this fast, PLEASE do not stand 90 degrees from any rotating shafts, and consider buying a bullet proof vest, and by all means wear safety glasses!
H001 set to 2. something u really need to do if u decide to run in sensorless vector mode. u set this once to do the tuning then it needs to go back to 0 when done; i do not recall if it turns off afterwards automatically or not. u look. BTW, ARE u running in sensorless vector mode? If not, this setting has no effect. I STRONGLY SUGGEST U NOT RUN IN THIS MODE UNTIL YOU HAVE EVERYTHING ELSE RUNNING PROPERLY FIRST! At this point you have no idea if tuning is the issue or parameter settings. get a good system running in v.hz mode first, THEN go to sensorless. Since you have major issues with settings right now, I see no valid reason to talk about sensorless mode or H001 at this time.
A044=? what? check out its meaning. default is 0 that is v/hz mode, so unless u changed it, H001 won't effect anything anyway! not till u set it to 3.
u can control both cw and ccw with M03/M04. you can do it by programming a frw and a rev digital input and provide a 0-10v speed command, all 3 from mach3.
B012=11? 8.6? units on this parameter are 20-100% of drive rated current..... so if u mean drive is rated 11 amps, and ur motor is rated 8.6, this paratemeter should be set to 8.6/11 *100= 78%. IT IS A SAFETY LIMIT PARAMETER NOT A CONTROL PARAMETER. It has no effect on motor performance. Set it to ur motor amp rating reduction from drive rating to help protect ur motor. so this setting is NOT causing E05.
u get E05 because ur settings are so far off base. prob that A003. no load, ur 8.6a motor should run at about 3 amps as shown on D002 current display - at any constant speed from 0 to base speed. since u see 10-13a u got something really wrong.
A082= ur motor rated voltage; did u change this one? most people do NOT need to change it. IF u cannot set it proper for ur motor, see A045 for tweak.
do these things and ur wj200 should come back to normal life.