This will be a PLC function.
normally this kind of behavior is optional controlled by the PLC I would recommend reading the parameter book or with the 0if control you can press SYSTEM -> PMC...
Type: Posts; User: MysticMonkey
This will be a PLC function.
normally this kind of behavior is optional controlled by the PLC I would recommend reading the parameter book or with the 0if control you can press SYSTEM -> PMC...
Quite often decent MTB's will have additional Mcodes pre defined in the PLC usually a latched type or a oneshot. Barfeeder integration should be much more than just an m-code with alarm codes for...
ಠ_ಠ
T1010
Dude.
If Fanuc restored the FROM then they should have also restored the CNC options
Then all you need is parameters, diagnostics and ladder (specific to YOUR machine) if it is a big machine you...
Daniel. please look at this thread
http://www.cnczone.com/forums/daewoo-doosan/262298-doosan-tech-docs-service-bulletins.html
kinda you need to be a bit more accurate than using the markers. you can get away with it for Z and B but the X & Y you should clock up with a DTI. also the X home position is not the same as the X0...
This is not a parameter problem this is zero position loss.
Organising a technician will be required to re position all the axes to their correct home positions then calibrating your tool setter,...
Ethernet on the 0i-MC is an option check you have it
depending what data you want out you can use DPRINT commands via RS232
cycle start button
I laugh every time I see a new post on this thread
There was never a poster offering software
He shared the sales information about the mgi simulator NOTHING ELSE
Stop asking for Fanuc...
I think this is more like what you are trying to develop.
MTB's like Hartford use this to create their HARTROL software.
I suggest you invest in a few Fanuc 30i series manuals
Programming...
!!!!!! What he said !!!!!!!
421 AXIS EXCESS ERROR
Usually caused by mechanical error lub, ballscrew, gib fault etc
Or error with encoder/scale
I think possibly there is a separate detector / scale on this machine ?
and the...
Contact your local Doosan dealership they will be able to get you a hard copy from Doosan hq
If it was the bus then it would power up and give you an alarm. I think your assumption that it is the power supply was correct. Which overload is tripping ? Is it before or after the hydraulics...
The fact you are getting FSSB number of amps is small error and a serial data error indicates there is a serious problem with one of the axis modules.
This is assuming the errors are related.
...
Hi, are you able to still get the old 3s live milling units ?
If so where from ?
Double check your Keep relays against the blue book,
specifically K6
or the G-data
SYSTEM -> PMC -> PMC PRM -> DATA -> G. DATA
There should be a procedure on changing G. DATA settings on one of...
This would only be 'unsafe' if you can run the machine with the doors open.
Which would mean the door interlocks are bypassed or faulty.
Having a switch to change M2/M30 into an M99 isn't...
It is shown in the H100 electrical manual
AH10H18BA05
AH10H18BB02
AH10H18BB03
AH10H18BB04
I have checked all the manuals up to SN:0256
they all show this
Your talking about Fanuc Ladder III right ? not Fapt Ladder.
If so....
Click File
Click Export
Select Memory-card format file
Click Next
Select the directory you want to save it to... I.E....
Using Parameters 3411 -> 3420 you can use any m-code to suppress the NC from processing all arithmetic expressions and conditional branches. yes M01 would be a good choice
alternatively parameters...
Generally the only different configurations come from the MTB side where they decide to have a crossed pair or something silly like this. I.E. patch cable from Fanuc to the sheet metal.
100% of...
Stevo1 is correct this is a custom macro alarm.
you would need to find the section in your macro #3000=87 and work backwards to find the cause
*edit:* Note: The lower 500's can also be...
You would need to tie these to one of the custom macro variables as you have said.
you would need a line in your ladder some thing like:-
R0031.0.......G54.0
---| |----------O-
...
There are a few options
1. Embedded Ethernet = FTP data transfer
2. Fast Ethernet + Data Server = FTP + EXTRA MEMORY
3. FOCAS Ethernet = 99% Remote CNC Operation
4. PCMCIA Ethernet adapter =...
I think the ladder is held on eprom chips on this model Fanuc
you would need to extract the code off these chips modify then write the code back to them.
refer to this post...
You need to look through the Ladder diagram specifically at the address list the D bits will be listed in this...
D304.0 = Red
D304.1 = Yellow
D304.2 = Green
According to my Electrical...
D304.0 = Red
D304.1 = Yellow
D304.2 = Green
Between [ PMCPRM ] and typing 62 you need to also press
[ KEEPRLY ] (to get you to the keep Relay screen)