Thank you.
I asked that to be tested. My customer is in a different continent and is late there already.
When I know the results, I will inform.
Thank you
Type: Posts; User: JohnBrownP
Thank you.
I asked that to be tested. My customer is in a different continent and is late there already.
When I know the results, I will inform.
Thank you
Once again thank you for the answer.
But from what I read, set #6 to 1 will mean that the program is assumed to be NOT completed when M02, M30 or M99 is found.
Would not this what we wanted to...
Yes program is completely received on the CNC.
Code is sent by my own software (that works ok on several other machines, using a null modem cable, as this one)
Parameter 3201 is currently set as:
...
Thank you for your information.
I have tested and the setting was on USE mode. I tested also in NOT USE and the result was the same.
I have attached the menu where the setting was changed. Maybe...
The current settings are attached (image) I hope this is the menu that you are referring to, but I do not find the related setting.
Thank you for your time.
Thank you for the answer.
You suggest that the PMCCNF it set to OFFLINE or similar? I am not near the machine so I do not know what to say to the end customer.
Thank you
Good morning. There is no other possible solution?
No one here that uses the same controller and serial port transfer?
I am still on the same spot as I was.
Thank you
It the machine needs home, i think the encoder is not absolute (I can be wrong).
If your current location is already overtravel, I recommend that you disconnect the machine and move manually (rotating yourself the screw) to a location that will overcome the limit.
Check if the...
Good morning.
This parameter, bit #6 (NPE) was already set as 0, so, unfortunately the proposed solution did not worked on this case.
Thank you. I will ask for bit #6 to be changed to 0.
I will reply if this fixed the issue.
My program ends in:
M30
%
so this is probably helpful. Thank you
Hello.
I have done this same setup on older controls (21 for example) and now I am trying the same on a very recent oi-TD.
Using a null model cable and setting up the serial transmission of a...