    Question Mori Seiki MSG 501 Fanuc 18 iTA - PCMDI language parameter

    Hello

    We changed 3102 but it was only change fanuc side language.

    Does anyone know the language change parameter of the PCMDI (Mori-Seiki side)?

    Any help would be very grateful.

  2. #2
    Join Date
    Feb 2009
    Posts
    6028

    Re: Mori Seiki MSG 501 Fanuc 18 iTA - PCMDI language parameter

    What language do you want?
    Should be keep relay 20 for alarm language but check YOUR ladder to make sure
    Attached Thumbnails Attached Thumbnails ladderlanguage.pdf  

  3. #3
    Join Date
    Feb 2009
    Posts
    6028

    Re: Mori Seiki MSG 501 Fanuc 18 iTA - PCMDI language parameter

    If you wish to have the MAPPS panel in a different language, you will need to contact your dealer and have them come out to install the correct language version of software.

  4. #4
    Join Date
    Apr 2015
    Posts
    18

    Re: Mori Seiki MSG 501 Fanuc 18 iTA - PCMDI language parameter

    hello,
    i need English language,
    and no mapps,
    need only PCMDI screen. it is containing magazine , atc manual operation and turnmill offset page, load monitoring etc.


    I will try your suggestion. thanks

    sorry for my English.

  5. #5
    Join Date
    Apr 2015
    Posts
    18

    Re: Mori Seiki MSG 501 Fanuc 18 iTA - PCMDI language parameter

    keep relay 20 are all zero, there is no effect.

  6. #6
    Join Date
    Feb 2009
    Posts
    6028

    Re: Mori Seiki MSG 501 Fanuc 18 iTA - PCMDI language parameter

    Pretty sure MSG 501 IS a mapps control. MSC was not. Sould be Mapps 1. Those are software driven, in fact during instalation of the software it never asked what language, so i think the software is specific for the region. This will get expensive i think. You will need to regester the machine with Mori Seiki (you will need to do this if you ever want to order parts anyways) then have the service tech come out with the proper mapps version and load it in to the machine. The keep relay is only for alarm messages.

  7. #7
    Join Date
    Apr 2015
    Posts
    18

    Re: Mori Seiki MSG 501 Fanuc 18 iTA - PCMDI language parameter

    keeprelay 20 not affect to alarm or something.

    thanks

  8. #8
    Join Date
    Aug 2011
    Posts
    2517

    Re: Mori Seiki MSG 501 Fanuc 18 iTA - PCMDI language parameter

    take photos of the screens and post here. if they are accessed with the custom button some of them were Fanuc screens and can probably be changed.
    on my MAPPS the language is set in one of the INI files and depending on what MAPPS version you have and what language and files you have now it may be possible to just copy across and replace one file from an English version of the MAPPS software.
    But first take photos of the screens so we can see what they belong to (Fanuc side or MAPPS side)
    Also if you can manage it, take out the PCMCIA card from the MAPPS unit, put it into a laptop and copy out a directory of all the files in a DOS command prompt by typing DIR /S > LIST.TXT
    then post the file LIST.TXT here. This will tell us what language files you have now.

  9. #9
    Join Date
    Feb 2009
    Posts
    6028

    Re: Mori Seiki MSG 501 Fanuc 18 iTA - PCMDI language parameter

    He sent me a message saying in fact its a MSC control, so no mapps. Just a keep relay setting.

  10. #10
    Join Date
    Apr 2015
    Posts
    18

    Re: Mori Seiki MSG 501 Fanuc 18 iTA - PCMDI language parameter

    Click image for larger version. 

Name:	IMG_20150424_203739.jpg 
Views:	44 
Size:	158.5 KB 
ID:	278210

    it is msc 501.


    subject was wrong. sorry.

  11. #11
    Join Date
    Feb 2009
    Posts
    6028

    Re: Mori Seiki MSG 501 Fanuc 18 iTA - PCMDI language parameter

    Its all in the back of the ladder book.

  12. #12
    Join Date
    Apr 2015
    Posts
    18
    Quote Originally Posted by underthetire View Post
    Its all in the back of the ladder book.
    Where can i find the ladder book?

  13. #13
    Join Date
    Feb 2009
    Posts
    6028

    Re: Mori Seiki MSG 501 Fanuc 18 iTA - PCMDI language parameter

    If your machine did not come with one, you will need to order one from Mori. They are machine specific.

  14. #14
    Join Date
    Apr 2015
    Posts
    18

    Re: Mori Seiki MSG 501 Fanuc 18 iTA - PCMDI language parameter

    hello
    pcmdi language issue Solved

    solution:

    1- enter the pc mdi screen
    2- hit the number keys "95" and input
    3- a screen message appear ( enter DATA
    4- write "196" and input
    5- D data 196 will appear on the screen
    there is 7 bits
    and all must be zero (0)
    0 input
    and save.

    voila!

  15. #15
    Join Date
    Apr 2015
    Posts
    18

    Re: Mori Seiki MSG 501 Fanuc 18 iTA - PCMDI language parameter

    but, allarma language still in japanese
    there ie no infor about that.

    thanks

  16. #16
    Join Date
    Aug 2011
    Posts
    2517

    Re: Mori Seiki MSG 501 Fanuc 18 iTA - PCMDI language parameter

    Keep Relay parameter K20 bits 0 and 1 probably need to be changed

    bit 0 = 0 With Language Select for Alarms
    bit 0 = 1 Without Language Select for Alarms

    bit 1 = 0 With Other Language
    bit 1 = 1 Alarms are English or Japanese

    the bits 2,3,4,5 should be all 0 but if ONE of them has a 1 it is used to set the language german, french, spanish, italian (in that order bits 2,3,4,5)

    Please tell us what settings you have in K20

    You may need to check your Fanuc parameter for language too.... 9924.0 to .7

  17. #17
    Join Date
    Apr 2015
    Posts
    18

    Re: Mori Seiki MSG 501 Fanuc 18 iTA - PCMDI language parameter

    hello

    K20 is all Zero,
    param 9924 was 0bit=1
    I changed 0bit to zero and system restart
    no effect for alarm.

    fanuc side English, PCMDI side English.
    only alarm ((
    thanks for your helps

  18. #18
    Join Date
    Aug 2011
    Posts
    2517

    Re: Mori Seiki MSG 501 Fanuc 18 iTA - PCMDI language parameter

    9924.0 is 1 for Japanese language so it should probably be 0 anyway. English = 9924 all bits are 0

    For english alarms K20 bit 1 should be 1
    K20 bit 0 could be either 1 or 0. probably should be 1 but the use isn't clear (i.e. "without language select" means what? it's fixed at English or Japanese or something else? Don't know exactly....)

    K20 should be 00000010 or 00000011

    try both ways and report back here with your findings. power machine off/on to test it after changing K20

  19. #19
    Join Date
    Apr 2015
    Posts
    18

    Re: Mori Seiki MSG 501 Fanuc 18 iTA - PCMDI language parameter

    I've tried both way with power off/on.

    EX alarms still japanese.

  20. #20
    Join Date
    Aug 2011
    Posts
    2517

    Re: Mori Seiki MSG 501 Fanuc 18 iTA - PCMDI language parameter

    Your machine may be different. Those parameters were from MSG-500 21iTA
    Do you have the ladder diagram manual? The PMC parameters are listed at the back.

Page 1 of 2 12

Similar Threads

  1. Need parameter for Mori Seiki DL-15 with Fanuc 16TT
    By greenery_fr in forum Mori Seiki lathes
    Replies: 2
    Last Post: 06-17-2022, 12:49 AM
  2. parameter back up for mori seiki zl45 fanuc OTTC
    By Asfar in forum Mori Seiki lathes
    Replies: 0
    Last Post: 01-27-2012, 09:56 AM
  3. CNC LATHE MORI SEIKI Diagnostic Parameter
    By suleman_mani in forum Fanuc
    Replies: 2
    Last Post: 05-19-2008, 08:47 AM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •